Step 3: The Light Comes "On" Again
Someone enters the same room near the switch at the right of the graphic. He or she flips that switch. Now there is again a pathway for the electricity. This time it flows over the second of the two wires running between the switches.
When you encounter what was supposed to be a three-way circuit, and you can turn it "on" at one of the switches, but not at the other switch, unless the first switch is already "on," the problem is usually that one of the wires going into the switch is on a terminal for one of the two wires going out of the switch.
Not all three-way switches are the same, either. All of them have two screws on one side of the switch and one screw on the other side. But, the screws for the wires running between the switches may be on the same side of the switch, or they may be on opposite sides of the switch at the same end of the switch. You cannot make assumptions. It is not uncommon to find that one switch in a three-way circuit uses one arrangement, but the other is from a different manufacturer and uses a different pattern for the screws.
If you have a continuity tester, you can shut "off" the circuit breaker and test the switch to determine which screw connects to what.
I helped a friend at his vacation home. He had a three-way switch at the top and bottom of a stairway. Since the time the home was built thirty years ago he has had to turn the switch at the bottom of the stairway "on" first. Then he could turn the light "off" or "on" from the top of the stairway where the bedrooms are. If the switch at the bottom of the stairway was "off," he could not turn the light "on" from the top of the stairway. The problem was what I mentioned above. The wire going into one of the switches was on a screw terminal for one of the wires going between the switches. In this case, I did not have any meters or testers, but had to reason out the problem. I got it solved in about ten minutes. He is happy now because his three-way circuit works as it should.
See the second image. This is an update. I discovered an exception to the rule that three-way circuit problems are due to two wires transposed into each other's place. The photo shows a dimmer switch that can be used as a single-pole switch or as a three-way switch. These switches fail in time due to overheating. When they do, the switch may work when the toggle is up or down, but not in both positions. This can make you think two wires are in each other's place, but the switch simply needs to be replaced. A continuity tester does not work on one of these switches. If you find one on a three-way circuit that is not working, just replace the switch and your problems will likely be solved.
<p>Levitron, Lutron, and everyone else who make switches should pay you, print this, and jam it in the package with their 3-way and 4-way switches. <br><br>Thank you; this is outstanding because it made something that was previously black magic into something that's actually pretty simple. :-)</p>
Thank you for looking and for commenting. I am glad it is useful to you. I understand the black magic part. When I worked for my father as his go-fer, I did not have trouble understanding 3-way switches. My father would try to explain 4-way switches to me, and I just did not get it. <br><br>I hope one day you will be able to troubleshoot someone's improperly wired 3-way switch and make it work. That person will look on you as a god. Everyone needs that now and then.
Dear Phil following my earlier post re:(4 pole switches).<br>I have just watched your youtube post on 4 way switches..<br>I must say what a god-send explanation on 'intermediate switches' ; (which my son has been tuitioned to call them,?)..<br>A priceless explanation.<br>&quot;Just by your use of calling feed wires, 'travellers'. I can now see the wood from the trees.!!<br>THANKS EVER SO MUCH Phil B...<br>Now i can explain it to my son, no problem.. <br>(Fantastic, simple, short &amp; Sooo easily explained.).<br>WELL DONE &amp; Cheers again Phil...<br>Stay Safe dear instructor friend.
<p>I am glad your problem has been solved. I do not have a video at YouTube, but I am glad to know there is a good video there on these switches. </p><p>I recently did an Instructable on how I added a reverse to the 12 volt child's toy electric vehicle for my grandson. I used a double pole, double throw switch to reverse the polarity to the DC motor. </p><p>Thank you for looking and for commenting.</p>
My son has just started an Electrical Installation course..? <br>I am a 'long-time ago' qualified electronic engineer..? lol. <br>The son has been learning to wire up switches to lights, resistance etc..<br>But a 2- way switch ( 3 wiring contacts 1 contact takes the conductor flow &amp; the other two contacts, where your choice of switchin from one conductor pathway to another).It was called a single pole-double throw, in my day..<br>He has been asking about a 4 contacts switch they call an 'intermediate switch'..<br>I always called it a double pole- double throw: &amp; it had a few various wiring possibilities..Dont quote me but i think he said ' it can only be switched on or of.'.His homework diagram on said; &quot;Intermediate switch,&quot; seems to have 2 seperate contact paths, each pole to pole, ALWAYS ON, (1 for say Neutral wire, the other Live; in A.C wiring; both running in parallel.)..<br>It therefore looks like if you clicked the switch, &quot;it would just short-circuit both conductor paths.?? VERY DANGEROUS &amp; IS OBVIOUSLY WRONG;<br>Especially if 1 is Neutral running &amp; the other Live..As his course is more Electrician than electronics.<br>I wonder if someone could explain what an 'intermediate switch' is please &amp; how it works.? Any help appreciated. <br>Apologies for my paragraph sized explanation..Soz &amp; Thanks.!!
<p>I just want to check that I can use an intermediate (4 way) switch as a 2 way switch by using one of the top connections as the common. Comments please.</p>
A 4-way switch could be used as a 2-way or on/off switch. But, if by common you mean the white wire or neutral, do not connect it to the switch, or you will get a direct short between the hot and the neutral. An on/off switch is installed in the path of the black or hot wire.
Great explanation but I must throw this one out there. An instructor presented His class with a Garage having 1 recpt. &amp; one keyless (bare bulb socket), and switch for control. <br>3 conductors connected Garage to House where opposite 3-way switch is located. Garage recpt. is constantly hot, Garage light controlled by 2 switches in House and Garage. Using only existing 3 conductors how does this work? I must add, no it doesn't meet accepted code requirements. If someone can schematic this out, I'll dig out my old notes to verify because I have forgotten how you cheat this in since I took the course 30 years ago. My instructor was an Electrical inspector in his 70s who took great pleasure in tormenting his protege's with problems such as this even when they obviously were against common code basics. In his time though a grounding, non-current carrying conductor was unheard of except in Submarines. <br> <br>Zapp
Phil B, <br>The problem &amp; violation as I'm sure you're aware of is polarity switch at ceiling outlet. In varied situations both lamp shell and bulb base can be both hot, both neutral, lamp shell neutral, bulb base hot (code), lamp shell hot, bulb base neutral (code violation). I haven't pulled notes showing ckt. with polarity switching receptacle as opposed to light socket, which was example instructor used to emphasize danger of switching and breaking neutral through switches. <br>Great explanation though. I too required old electrician's drawings &amp; advice to fully understand that VooDoo, WhoDoo of the multiple location switch points and the various legal wiring methods of same. Great Instructable I'm sure helped many actually understand how &amp; why it works. Original multiple switch, Pull Chain Keyless in multi floor apt. house with long chain down staircase! <br>Zapp
The image in my response below shows a &quot;hot 3-way switch&quot; circuit. I believe it is what Zapp had in mind. I found it on the Internet by searching for &quot;hot 3-way.&quot; When I was my father's helper back in the 1960s, he often spoke of these. I have never seen one.
&nbsp;Excellent. &nbsp;Whenever I wire a three-way I always have to go look it up on the box. &nbsp;
Thanks.&nbsp; It would be great if the images in this will enable you to bypass looking at the box.&nbsp; <br />
Ha Wow, I finally get how it works! It makes sense now!
Thanks for your comment. I am glad to have been of help.
Your welcome.:)
Sweet! Thank you so much for explaining this, clear and concise. I feel like I've been "instructed." :-)
Thank you. I am glad it was clear for you. Once you know this, you can use it to do things, like correct a three-way switch that is never worked correctly.
Wow, so obvious, yet I had no idea. Thanks!
Glad to have been of help.
thank you whoever did this thing on 4 way switches. i figured a 4 way switch had 4 terminals, but i couldn't figure how it actually "switched" without leaving a completely open circuit. i think you made 4 way switches' concept very easy to understand. thanks again, josh -south carolina (united states)
You are welcome. I am glad it was easy to grasp. My father did electrical work and farmed in a rural area of Iowa. I was his helper all through junior high to college. I have 57 other Instructables, all of which are something practical. You might be interested in some of those, too.
Thats not how they are wired here in NZ. Also if there are 2 switches it gets called a 2 way switch here since there are 2 switches. What they do is wire one of the switches normally, to add 2 way capabilities a piece of 3 conductor cable is taken from there to the other switch location, and 1 is connected to 1, 2 to 2, and C to C - the cable is red/white/blue since they are allowable phase colours (yellow used to be but in harmonisation with Aussie it was decided not to be since its easy to mistake for a green/yellow earth) Anyway, then the power is connected to the 1 terminal of one switch, and the 2 terminal takes the power out to the lamp. This is done since its normal that the power goes in and out of the same flushbox rather then taking a single conductor to the other end. It is sometimes done the way described with a wire joiner taking the cable to the C of the remote switch to the cable out to the light, but thats not how new installs are done.
I thought about how you wire 2-way switches in New Zealand. Then I went looking for an example of it on the Internet. Is this what you do (2nd or bottom schematic)? <a rel="nofollow" href="http://www.diynot.com/wiki/electrics:lighting:two_way_lighting">http://www.diynot.com/wiki/electrics:lighting:two_way_lighting</a><br/>
Yeah, thats the one (second in the top image) - sometimes it will go thru intermediate switches which just connect to the wires between the 1 and 2 terminals
Thanks.
I am not sure why we call them 3-way and 4-way switches in the USA, but we sure do. My graphic is more of a schematic than a plan for routing wires. Certainly we most often use three strand cables between the switches. What connects to what depends on the layout of the building and where the light, the switches, and the circuit breaker are in relation to one another.
We call them 3-way switches because switches are already 2-way (On/Off)
Excellent,thanks
Thanks to Acme School of Stuff, I understood three-way. But, four-way completely baffled me. Thank you so much for clearing it up.
Thank you, this always bothered me...
I do not think you are/were alone by far. My father did electrical work and I often went with him as his assistant. I have met plenty of people who puzzled over how these things work. It is not that hard, once you grasp the concept. Thanks for your comment.
Thanks Phil! I could never picture how these work in my head, this is excellent.
Thank you. If you like being able to understand what may have been mysterious, wait until you amaze your family and friends by making a 3-way switch circuit work that never worked before. You will achieve rock star status. I think, too, the idea of comparing these circuits to a crossover at an Interstate construction zone makes it clear in one's mind.
About This Instructable
83,347views
35favorites
License:
Bio: I miss the days when magazines like Popular Mechanics had all sorts of DIY projects for making and repairing just about everything. I am enjoying ... More »
More by Phil B:Easy Monitor for NordicTrack Skier Uses for Spent K-Cups Make a Conduit Bender
Add instructable to: